ceb58
Senior Member
- Location
- Raeford, NC
At our communication sites there are taps on the single point underground halo. These taps are then welded to the tower legs, fence post and gates. They are also lugged to A/C units. One is then bonded with the service neutral in the service disconnect. As a rule all of these taps are sleeved in NMFC (car-flex) for looks and protection. We have found that some of the contractors have used LTFMC (Liquid tight) with the metal spiral inside. All they have done is mashed the ends and sealed the ends with duct seal. The conduit stops before the weld and is only about 12" underground. Would this not be a violation of 250.64 (E)?