Ground conductor Insulation

Status
Not open for further replies.

Gmk

Member
I have a cable pull consisting of 3 #2 5KV Cables with a #6 ground. These are going to be pulled through a conduit. My question is does the ground also have to be a 5KV rated insulation?
 

SEO

Senior Member
Location
Michigan
I don't think that it matters Section 300.3 (C) conductors of different systems refers to circuit conductors a ground wire is not a circuit conductor. Is it a metal conduit.
 

erickench

Senior Member
Location
Brooklyn, NY
Okay, NEC 250.118 states that the equipment grounding conductor shall either be run with the circuit conductors or enclose the circuit conductors. By enclosing they mean metal conduit and tubing. The metal raceways can be used as an equipment ground conductor providing that continuity i.e. good bonding, is maintained.
 