Re: Ground current check
Brian, it's a boost to see that someone else knows these N/G connection sources. That's a great list. I was saying "yes, yes". I spend so much time trying to tell other electricians about these errors, just to bring it to their awareness.
I would only add - two neutrals from different branch circuits connected together (you mentioned from different panels, which I have seen also). Also, neutrals mixed up in a junction box, with the wrong neutrals connected with the wrong hots.
Here's a variety of the nail scenario: the electrician was called in to deal with a short. A sheetrock nail had shorted the hot to the GEC. His solution: Don't bother to dig into the ceiling, just switch terminations in the panel and use the grounded conductor as the hot, and the hot as the grounded conductor. This left the (now) black grounded conductor still shorted to the GEC, resulting in net current fields. You can't fool a gaussmeter.
And Bennie, I know this would not result in a magnetic field unless the GEC was also interconnected with other metallic paths: it was.
Brian, about your flex CTs. I was also frustrated once because I could not get the 3' flex around a bus duct. (Though by taking a few gaussmeter measurements I could estimate the net current). I had two flexes, so I experimented when I got back to my lab, and found that you can connect two in series and that works.
Karl