R Rock86 Senior Member Location new york Occupation Electrical Engineer / Electrician Nov 10, 2020 #1 Could anyone recommend a Ground Detector for a 480V ungrounded system, other than Bender Isometers? The ISO685 would do way more than what I need it to do, but I am having trouble finding anything which could handle a 480V input.
Could anyone recommend a Ground Detector for a 480V ungrounded system, other than Bender Isometers? The ISO685 would do way more than what I need it to do, but I am having trouble finding anything which could handle a 480V input.
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Nov 10, 2020 #2 Three 480 volt transformer type pilot lights connected in a wye with the center of the wye connected to the EGC, and the ends connected to the phases.
Three 480 volt transformer type pilot lights connected in a wye with the center of the wye connected to the EGC, and the ends connected to the phases.