Am I interpreting 690.47(a) of 2017 NEC correctly in assuming that our ground mounted arrays should now have two ground electrodes installed (since the rack is considered a 'structure supporting PV array')? We usually build them on helical piles and galvanized pipe, but the piles usually only go about 4' or 5' into the ground.
Also, in scenarios where we have more than one ground mounted arrays located near each other (less than 10' or so), should we be putting (2) grounding electrodes at each array? The arrays are bonded to each other via an EGC.
(A) Buildings or Structures Supporting a PV Array. A building or structure supporting a PV array shall have a grounding electrode system installed in accordance with Part III of Article 250.
Also, in scenarios where we have more than one ground mounted arrays located near each other (less than 10' or so), should we be putting (2) grounding electrodes at each array? The arrays are bonded to each other via an EGC.
(A) Buildings or Structures Supporting a PV Array. A building or structure supporting a PV array shall have a grounding electrode system installed in accordance with Part III of Article 250.