enteng14 said:still the AHJ has this power and authority to implement above the code for public safety.
That is rarely true, if ever.
That is like saying police chiefs can make up laws as they see fit.
enteng14 said:still the AHJ has this power and authority to implement above the code for public safety.
enteng14 said:Where in the code states that you are not compliance if you only have one ground rod as grounding electrode? I believe the code only require the additional ground rod for more than 25 ohms measured resistance on the single ground rod.
As what sir infinity said that two ground rod is the simplest grounding electrode system but it doesn't mean that a single ground rod is a violation in the code. Two ground rod is better than one because of combined lower resistance.
enteng14 said:Where in the code states that you are not compliance if you only have one ground rod as grounding electrode? I believe the code only require the additional ground rod for more than 25 ohms measured resistance on the single ground rod.
As what sir infinity said that two ground rod is the simplest grounding electrode system but it doesn't mean that a single ground rod is a violation in the code. Two ground rod is better than one because of combined lower resistance.
weressl said:It's just to show ya how silly the Code can get sometimes and people who are arguing it, with it.:grin:
iwire said:Now how about that, we agree on some things. :grin:
iwire said:Now how about that, we agree on some things. :grin:
Your next stop :grin:weressl said:Not the first time either, you better watch out Bob! You got a reputation to maintain........:grin:
#6, #6, and #6.enteng14 said:What would be the size of the GEC for single ground rod as grounding electrode and for two ground rod installation? Also, what is the size of the jumper between the two ground rods?
I disagree (if only to be counted among the people who, as Weressl pointed out, are just being silly by arguing such thingsacrwc10 said:If you don't test the ground rod you can not say it has 25 ohm's or less, That would make a single rod a non compliant installation.
charlie b said:I disagree (if only to be counted among the people who, as Weressl pointed out, are just being silly by arguing such things). That is not what the code says.
If a single rod has a resistance under 25 ohms, it is code compliant. If a single rod has a resistance over 25 ohms, it is not code compliant. If I do not measure the resistance of a single rod, then I do not know whether the installation is code compliant or not. To simply say that it is not compliant is saying more than can be known.
This is one place in which the AHJ can throw around some weight. The AHJ can place the burden of proof upon the installer. The AHJ can declare that, "Not knowing whether this is compliant is not an acceptable situation. Either prove it is compliant as-installed, or make the compliance beyond question." That is the reason that it is good advice to simply install the second rod and be done with it.
ronaldrc said:I'm not near a code book but doesn't the code call for a backup or supplimental ground?
charlie b said:I disagree (if only to be counted among the people who, as Weressl pointed out, are just being silly by arguing such things). That is not what the code says.
If a single rod has a resistance under 25 ohms, it is code compliant. If a single rod has a resistance over 25 ohms, it is not code compliant. If I do not measure the resistance of a single rod, then I do not know whether the installation is code compliant or not. To simply say that it is not compliant is saying more than can be known.
This is one place in which the AHJ can throw around some weight. The AHJ can place the burden of proof upon the installer. The AHJ can declare that, "Not knowing whether this is compliant is not an acceptable situation. Either prove it is compliant as-installed, or make the compliance beyond question." That is the reason that it is good advice to simply install the second rod and be done with it.
ronaldrc said:Is it just water lines Bob?
infinity said:Article 250 requires that the rod have a resistance of 25 ohms or less or it must be augmented by another rod or electrode. If you don't want to actually test the single rod you'll need to install a second one.