Ground Enhancement Material use in a grounding network

Status
Not open for further replies.

t_van

Member
Had an engineer tell me that ground enhancement material must be used on the bare grounding conductors that are interconnecting ground plates and not just the ground plates in order to achieve the desired resistance to ground in a grounding network. Thoughts? Opinions? Facts?
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Had an engineer tell me that ground enhancement material must be used on the bare grounding conductors that are interconnecting ground plates and not just the ground plates in order to achieve the desired resistance to ground in a grounding network. Thoughts? Opinions? Facts?

might be true. depends on the earth properties and what the desired resistance is.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
But, on the other hand, the total area of the bonding conductors may not be significant unless the runs are long.
If the area is significant, and the soil itself is poor, then at that point adding enhancement materials would be justified.


Sent from my XT1585 using Tapatalk
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
if you do what he wants and it does not work it is on him.

if you do something else and it does not reach the desired resistance, you get to dig up the grounding system and redo it.
 
Status