Ground Fault and Total Harmonic Distortion

spikes2020

Member
Location
Nashville, TN
Occupation
Electrical Engineer
We have a weird issue, 2 breakers, a feeder in a sub and the main in a panel for some equipment. The feeder breaker is set to 300A ground fault at 0.2 second trip time, while the main in the panel is set to 1200A and 0.1 second. The main panel breaker is tripping first on GF. This is random trips while in operation and there appears not to be any ground faults on the system.

Under further investigation i see that this panel has 30-50% THD on each phase and it is reporting close to 500% TDD. Looking at the harmonics its 3, 5, 7th are crazy high and i assume these are from AC-DC rectifiers, most likely this is from VFDs or power supplies.

This is a 1000A 480V breaker, that most likely feeds several motors (single and 3 phase), plc's, and lots of other equipment. I think they are only pulling maybe 100-150A.

What would be recommended ways to solve this problem? Cap-inductor filters? Isolation transformer? Replace VFDs? Neutral-grounding resistors?

1765975630658.png
1765975545411.png
 
Have you confirmed the proper installation of the neutral CT on these breakers. I am amazed at the number of installation errors with these CTs, typical problems are surrounding all neutral conductors to not being wired with proper polarity.
 
Have you confirmed the proper installation of the neutral CT on these breakers. I am amazed at the number of installation errors with these CTs, typical problems are surrounding all neutral conductors to not being wired with proper polarity.

The sub breaker is where i am taking these readings it was just installed to feed this new equipment. I looked at the sub main breaker meter that was installed a long time ago and it has similar readings. These readings are from the CTs in the breaker its self and it only has 3 CTs, one on each phase. This equipment gets tested every 3 years so i am 99.9% confident that it is accurate. The panel breaker dose not have a way to get readings only the sub feeder and the sub main.
 
These readings are from the CTs in the breaker its self and it only has 3 CTs, one on each phase.
If the source is a grounded wye, your breakers should have a CT for each set of conductors or they need to be programmed as 3W devices. When programmed as 3 wire they might not show In current, so I would confirm their setup. Testing agencies typically test per the breaker settings, they rarely question if those settings are proper.

I have seen many more breaker install and setting errors than I have problems with load harmonics.
 
If the source is a grounded wye, your breakers should have a CT for each set of conductors or they need to be programmed as 3W devices. When programmed as 3 wire they might not show In current, so I would confirm their setup. Testing agencies typically test per the breaker settings, they rarely question if those settings are proper.

I have seen many more breaker install and setting errors than I have problems with load harmonics.

Ill look at that, but the sub feeder breaker that i am getting these readings isn't tripping, its the panel breaker at the equipment tripping on 1200A ground fault. The panel breaker is only 3 phases and is a insulated molded breaker with only basic settings, see below for settings.
1765979366760.png

Also i looked at another substation that is feeding more of this new equipment and getting similar readings. It has a newer meter. So i think these readings are accurate.
1765979217458.png
 
The only time I've seen a large breaker tripping randomly on ground fault, one of the feeder conductors had a gouge in the insulation. Replaced the conductor and never had another problem.

For your situation, not sure why the 300A breaker has more delay than the main - usually the main has more delay to allow the branch breaker to trip first. Also, do all the other feeder breakers have ground fault sensors?

But those harmonics do sound really high. In particular 5,7 and 11. According to this Siemens paper, three phase bridge rectifiers have harmonics at those particular frequencies. Not sure if this paper would be any help, but I think i would be trying to narrow down where those harmonics are coming from.

 
The only time I've seen a large breaker tripping randomly on ground fault, one of the feeder conductors had a gouge in the insulation. Replaced the conductor and never had another problem.

For your situation, not sure why the 300A breaker has more delay than the main - usually the main has more delay to allow the branch breaker to trip first. Also, do all the other feeder breakers have ground fault sensors?

But those harmonics do sound really high. In particular 5,7 and 11. According to this Siemens paper, three phase bridge rectifiers have harmonics at those particular frequencies. Not sure if this paper would be any help, but I think i would be trying to narrow down where those harmonics are coming from.


Thanks! Yeah all AC-DC machines (rectifiers) have bad 5 and 7th harmonics, so i am assuming the cause is a VFDs or power supplies or both. But for this size load what solutions do i have? I would like to give a solution tomorrow in our meeting and all i have is a big Capacitor-Reactor filter. I was wondering if there was newer tech out there to solve this issue. I think this equipment was built using cheap Chinese VFDs that are causing this problem and replacing those is a solution but i don't think we are going to go for that one.

I think they jacked up the current to 1200A to stop it from tripping so much. There isn't a ground fault on the system or we would know.... 1200A makes a bit of a spark. I'll get the coordination back in line once we solve the harmonic problem.
 
TDD. Looking at the harmonics its 3, 5, 7th are crazy high and i assume these are from AC-DC rectifiers, most likely this is from VFDs or power supplies.
3rd order harmonics in VFD rectifiers self-cancel. 3rd order mostly come from single phase non-linear loads, such as power supplies, UPS, electronic ballasts and LED drivers. Better load balancing can help ameliorate that.

I find that when you have a THD problem on existing systems, it’s often best to deal with it using Active Harmonic Filters. They don’t care about the source or order, they simply see and react to cancel them. Several of them now also will help correct power factor as well.
 
At first I was thinking maybe your system had a resonance that was enhancing harmonic currents, where power factor correction capacitors were interacting with the system inductance. But if so, I'd expect to have a higher level of voltage harmonics as well. The voltage harmonics shown seem almost too perfect given the level of current harmonics. Every L-L and L-N has the identical 1.3% amount of voltage THDv. If that's true, maybe the impedance that's driving this feeder is very low, and there are no DC link chokes or line reactors to help limit the amount of peak current from the rectifiers.

Given how high level the harmonics are, I think it could be useful to have a 'scope to look at the current waveforms, and perhaps at individual machines as well. You could see if there's any ringing or other behavior that's different than expected from normal 6-pulse rectiifers.

Perhaps it would be best to include link chokes or line reactors to reduce the current peaks, and consider Active Harmonic Filters as @Jraef mentioned which will dynamically apply currents to cancel out the THDi.
 
At first I was thinking maybe your system had a resonance that was enhancing harmonic currents, where power factor correction capacitors were interacting with the system inductance. But if so, I'd expect to have a higher level of voltage harmonics as well. The voltage harmonics shown seem almost too perfect given the level of current harmonics. Every L-L and L-N has the identical 1.3% amount of voltage THDv. If that's true, maybe the impedance that's driving this feeder is very low, and there are no DC link chokes or line reactors to help limit the amount of peak current from the rectifiers.

Given how high level the harmonics are, I think it could be useful to have a 'scope to look at the current waveforms, and perhaps at individual machines as well. You could see if there's any ringing or other behavior that's different than expected from normal 6-pulse rectiifers.

Perhaps it would be best to include link chokes or line reactors to reduce the current peaks, and consider Active Harmonic Filters as @Jraef mentioned which will dynamically apply currents to cancel out the THDi.

This is good advice and the active filter advice too. The white paper is mostly what i thought and is good to be able to backup my story. I looked at the other substation that is feeding this equipment and its voltage THD is not bad either, around 1-4%. Main voltage harmoics are 5 and 7th.

1766062450501.png

I think we might have some single phase VFD motors that might be the problem. I think between the white paper and the few ideas given here we have a direction to go. Thanks everyone!
 
I've had a ground fault issue happen due to an elevator in the building also. May not apply, but something to think about.
 
One last thing (long shot), does anyone have that white paper in Japanese? or something that discusses the same stuff in Japanese?

I am trying to explain it to them but hitting a wall.

I am afraid to run it all though a translator and get gibberish out the other end. Technical documents never do well in translators.
 