Coordinating Protective Devices
Coordinating Protective Devices
I meant to say that should the feeder ground fault relay be coordinated only with the upstream main ground fault relay, or should the feeder ground fault relay be also coordinated with upstream main overcurrent relay?
Feel free to correct me if I'm wrong.
Are your Ground Fault relays for breakers over 1200A?
I recently ran a coordination study for a large hospital. Per adopted code we needed to have Ground Fault protection on all breakers over 1000A(not sure when this was adopted but 230.95) During my study I had to coordinate all the breakers from MDP (3000A) down to 70A (starting at 0.1sec). It's really difficult coordinating small breakers due to the lack of electronic trip sensors below 60A I believe. If you have a power system analysis software (skm,easypower) you can visually see the coordination curves. I remember my LSIG (long,short, instantaneous, ground fault) breakers didn't have the flexibility/range as the smaller breakers to coordinate in the long term region which helped for coordination.
For me, as long as I used the same manufacturer (Eaton,SQ D) my curves were easy to coordinate using electronic trip units. I can't say I remember reading it in NFPA code but our Eaton rep explained it to me that all regions on your TCC curves needed to be coordinated (starting at 0.1 sec, unless life safety then it's 0.01 sec) except very small breakers that simply can't achieve coordination.