Is there a formula to calculate 480V, 3-phase ground fault current at specific panel bus, motor bus? I tried to meet this rule below by setting GF level at electronic CB... Is there a minimum ground fault level setting per NEC?
Settings of the ground fault device(s) are limited to a maximum of 1200A pickup and one second delay for ground faults greater than 3000A (NEC 230.95A).