Is this reason for Ground Fault Current???Gotcha! Your cable layout is not the optimal arrangement for flat multi-cable runs. Here is the proper arrangement:
View attachment 2560020Or you could arrange your cables in A1B1C1 A2B2C2 A3B3C3 with intra-phase spacings of 2 cable diameters apart, cable groups (1 to 2 and 2 to 3) with 3 cable diameters apart. But definitely not the way you did as shown in your sketch.
Hope that helps!