thunder15j
Member
- Location
- Cali
We service several older electrical systems that are 480 volt 3 phase systems, some 240 volt systems, that are fed from our Poco by 3 wire ungrounded systems. (I've mentioned this in other posts) Our customer gear is rated 3 phase-3 wire. 100 and 200 amp meter sockets are 5 jaw. The systems are typically 480 volt Delta. Bear in mind that these systems are typically 25+ years old As per NEC 250.21 ground detection is required on these systems today but probably not when they were installed.
In the pursuit of safety on the 480 volt systems, we have installed a pilot lit ground fault detection system which consists of three 480 volt pilot lights connected L1-ground, L2-ground, L3-ground. On normal circumstances they will be dimly lit. Also a PTT(push to test) connection is made across 480 volts to prove the lamps will burn brightly when a fault would occur. In the event of a detected ground fault, one of the three lamps will go out and the other two will burn brightly. The equipment wiil keep running but the operator is now aware that a fault exists and must be promtly repaired. This is a configuration that I got off the MSHA site. It seems to work quite well.
I'm wondering what other ground detector systems are out there.
Also would this work on an ungrounded wye configured transformer that the Poco has provided? Customer gear is also 3 wire-3 phase.
Funny thing on this installation: I was getting ready to install the 3 light detection system and noticed I was getting 277 to ground on all three legs. Poco says that the neutral bushing on their transformer is not connected to ground and they have only three wire coming into the service gear. Poco says something about an induced voltage (cannot use the actual word on this site; b------ voltage ). Voltage was measured with Fluke 117 in low impedance mode.
In the pursuit of safety on the 480 volt systems, we have installed a pilot lit ground fault detection system which consists of three 480 volt pilot lights connected L1-ground, L2-ground, L3-ground. On normal circumstances they will be dimly lit. Also a PTT(push to test) connection is made across 480 volts to prove the lamps will burn brightly when a fault would occur. In the event of a detected ground fault, one of the three lamps will go out and the other two will burn brightly. The equipment wiil keep running but the operator is now aware that a fault exists and must be promtly repaired. This is a configuration that I got off the MSHA site. It seems to work quite well.
I'm wondering what other ground detector systems are out there.
Also would this work on an ungrounded wye configured transformer that the Poco has provided? Customer gear is also 3 wire-3 phase.
Funny thing on this installation: I was getting ready to install the 3 light detection system and noticed I was getting 277 to ground on all three legs. Poco says that the neutral bushing on their transformer is not connected to ground and they have only three wire coming into the service gear. Poco says something about an induced voltage (cannot use the actual word on this site; b------ voltage ). Voltage was measured with Fluke 117 in low impedance mode.