I have been reading a lot about grounding and bonding and watching Mike Holt's videos on the subject. In his videos Mike talks a lot about grounding safety misinformation.
He says that properly grounding the circuit will not open the breaker in the event of a fault.
Then, I ran into this sentence in the DOE (Department of Energy) Electrical Safety Handbook page 55:
4.4 BONDING
Caution shall be taken to ensure that the main bonding jumper and equipment bonding jumper are sized and selected correctly. Bonding completes the grounding circuit so that it is continuous. If a ground fault occurs, the fault current will flow and open the overcurrent protection devices.
Is this the kind of misinformation which Mike Holt is referring to in relation to grounding?