I'm preparing for NEC Exam, on practice questions I always get the following question wrong, can someone help me understand why ....
Q: Ground-fault protection of equipment shall be required for a feeder disconnect if _____?
a) the disconnect is rated 800A, 208V
b) the disconnect is rated 800A, 480V
c) the disconnect is rated 1,000A, 208V
d) the disconnect is rated 1,000A, 480V
I go to the correct code section 215.10, but always answer "C". I think I'm associating 208 with a wye system and 480V with a delta system.