A source of some confusion for me is the idea of GFP for inverters interconnected on the load side of a service entrance OCPD.
705.32 says: Where protection is installed in accordance with 230.95 the output of an interactive system shall be connected to the supply side of the ground-fault protection.
Exception: Connection shall be permitted to the load side of ground-fault protection if there is ground fault protection for equipment from all ground-fault current sources.
One consultant tells me that that means we need GFP on our load side interconnection breaker and another tells me that the SMA inverters we are using have GFP, so we do not. The data sheet for the inverter says it has ground fault monitoring: Riso/Differential current, but I am not sure that it means that it has GFP on the AC side so 705.32 is covered; the line on the data sheet does not say if the ground fault monitoring is on the AC side, the DC side, or both.
What say you?
705.32 says: Where protection is installed in accordance with 230.95 the output of an interactive system shall be connected to the supply side of the ground-fault protection.
Exception: Connection shall be permitted to the load side of ground-fault protection if there is ground fault protection for equipment from all ground-fault current sources.
One consultant tells me that that means we need GFP on our load side interconnection breaker and another tells me that the SMA inverters we are using have GFP, so we do not. The data sheet for the inverter says it has ground fault monitoring: Riso/Differential current, but I am not sure that it means that it has GFP on the AC side so 705.32 is covered; the line on the data sheet does not say if the ground fault monitoring is on the AC side, the DC side, or both.
What say you?