JdoubleU

Senior Member
If there is a gound fault at a receptical, What are the reasons the breaker will not trip. One of our offices had a bad receptial. When I had arived the breaker had arced and melted some of the metal box. The breaker did not trip. I know that breakers are designed to handle a high inrush current and that sometime the arc does not draw enough current to trip a breaker. Is it also possible that the ground path is not good.
 

raider1

Senior Member
Staff member
Location
Logan, Utah
How old is the breaker and what brand is it?

This does sound like it could be a high impeadance ground fault current path.

Chris
 

al hildenbrand

Senior Member
Location
Minnesota
Occupation
Electrical Contractor, Electrical Consultant, Electrical Engineer
the breaker had arced and melted some of the metal box. The breaker did not trip.
I do, among other things, consulting for a national magazine. To illustrate this very thing, for a story editor, I hooked up a simple plug and cord 1500 Watt electric space heater to a photo set (mocked up) receptacle.

I supplied this photo set with a simple cord to a 120 V 20 A circuit.

I loosened one terminal screw to conductor connection on my photo set receptacle, just so, and turned on the heater.

The heater ran, the breaker did not trip, and this little tiny plasma arc shown at the loose terminal screw and slowly ate away at the copper and screw.

I kept it running that way for about 10 minutes until the receptacle was "photo ready".

The more common name for this type of connection is "glowing connection". Try googling it.
 

JdoubleU

Senior Member
How old is the breaker and what brand is it?

This does sound like it could be a high impeadance ground fault current path.

Chris

What would be the best way to measure the resistance of the EMT that is being use for the ground.
 

bob

Senior Member
Location
Alabama
If you want the DC resistance you could use an ohm meter. However, the impedance of the conduit varies with the magnitude of fault current. In your case the arc has an impedance value and thats probably why the breaker did not trip. If you are interested in the calculations for the conduit, check here
tonight and in a short time you will sleep soundly.
http://www.steelconduit.org/pdf/groundingpart1.PDF
 

JdoubleU

Senior Member
If you want the DC resistance you could use an ohm meter. However, the impedance of the conduit varies with the magnitude of fault current. In your case the arc has an impedance value and thats probably why the breaker did not trip. If you are interested in the calculations for the conduit, check here
tonight and in a short time you will sleep soundly.
http://www.steelconduit.org/pdf/groundingpart1.PDF

In your opinion do you think that it was just the impedance of the ARC that the breaker didin't trip and not the impedance of the ground. It was a pretty nasty arc that left about a quarter inch hole in the metal box. My Boss said if was not a poor ground, but I have seen arcs in outlet boxes that would trip the breaker right away.
 

Cow

Senior Member
Location
Eastern Oregon
Occupation
Electrician
What would be the best way to measure the resistance of the EMT that is being use for the ground.

Can't you just continuity test between the neutral and the metal box? Or drag a ground wire from the panel and test from that to the metal box?
 

bob

Senior Member
Location
Alabama
In your opinion do you think that it was just the impedance of the ARC that the breaker didin't trip and not the impedance of the ground. It was a pretty nasty arc that left about a quarter inch hole in the metal box. My Boss said if was not a poor ground, but I have seen arcs in outlet boxes that would trip the breaker right away.

IMO You had an impedance in the ground fault path or a bad breaker.
 

kwired

Electron manager
Location
NE Nebraska
Can't you just continuity test between the neutral and the metal box? Or drag a ground wire from the panel and test from that to the metal box?

you would need to take into consideration the resistance of the neutral wire or test wire you mentioned.

And this would just give you the DC resistance not the impedance of the AC scenario which will have other varying factors besides resistance alone.
 

HotConductor

Senior Member
Location
Philadelphia
Does this originate from a main panel and is the main bonding jumper in place and properly connected with the correct machine screw or bolt/nut? This is critical for clearing ground faults.

I just opened up three panels two weeks ago after a 4kv line dropped across two 240v lines and sent 4kv into these panels and found a drywall screw holding the main bonding jumper to the can.
 