I am being asked by POCO to relocate a meter to the back of a house and run a conduit from the new meter location to the existing panel. Do I need to run a ground from the panel to the meter can? The ground rod is driven and terminated at the panel location.
I'm seeing a "different" question.
If you are relocating the meter but leaving the panel in the same location, my question is how are you routing the cable between the meter and the panel. 230.70 requires the service disconnect outside or inside nearest the point of entrance. To comply are going have to add a service disconnect ahead of the existing panel ??
If so, you will need a separate equipment ground to the old panel and your grounding electrode conductor would need to terminate at or prior to your new disconnect.
Am I reading something in that isn't in your post ?
I am going to install emt on the exterior of the house from the new meter location to the old meter location and use the old meter box as a junction box into the back of the panel. The meter is moving down the same wall about 30feet. The service drop is getting pushed and encased by ice in the winter, so poco wants the drop closer to the pole. The existing panel will stay in place and still be the service for the house.
That is strange to me. As I have said on numerous occasions, each electric utility is different.. . . poco wants meter below mast. . .