Strahan
Senior Member
- Location
- Watsontown, PA
Few questions and concerns: Under 680.26(B)(1)(b) it explains how to construct a copper conductor grid for in the conductive swimming pool shell. In it it says if the rebar is encapsulated with a non conductive coating this grid must be installed.
(1) can the grid be attached directly to the rebar system for support?
(2) It says the #8 bare solid copper wire is to be bonded together at all points of crossing with a 12 X 12 perpendicular grid pattern. It doesn't say how each point of intersection is to be connected.
(3) While it may be easiest to just form the grid out of uncoated rebar some problems exist with this type of installation. The rebar is to be connected at points of intersection with a steel tie wire under 680.26(B)(1)(a). Over time, rebar in concrete rusts to possible entire deterioration. How is the grid maintained as a continuous unit if the connections are no longer made?
Thanks in advance for any comments!
(1) can the grid be attached directly to the rebar system for support?
(2) It says the #8 bare solid copper wire is to be bonded together at all points of crossing with a 12 X 12 perpendicular grid pattern. It doesn't say how each point of intersection is to be connected.
(3) While it may be easiest to just form the grid out of uncoated rebar some problems exist with this type of installation. The rebar is to be connected at points of intersection with a steel tie wire under 680.26(B)(1)(a). Over time, rebar in concrete rusts to possible entire deterioration. How is the grid maintained as a continuous unit if the connections are no longer made?