iggy2
Senior Member
- Location
- NEw England
The Code generally requires a "low impedance" path to ground, via an equipment grounding conductor (which can be of many forms - a conductor, RGS, EMT, etc. per 250.118). Is there any standard on what constitutes a "low impedance"??? The only definition I see is for "Effective Ground-Fault Current Path", which uses the term 'low impedance.
I am involved in a situation where existing equipment grounding conductors (via metallic raceways) is, worst case, about 1/10 of an ohm. Other readings are lower. It has been suggested that these values are unacceptable, and a copper EGC be added to the raceways, and I am trying to judge if these values are in fact unacceptable.
The grounding electrode impedance is 2.5 ohms, so that is not in question (unless because it seems unrealistically low...)
I am involved in a situation where existing equipment grounding conductors (via metallic raceways) is, worst case, about 1/10 of an ohm. Other readings are lower. It has been suggested that these values are unacceptable, and a copper EGC be added to the raceways, and I am trying to judge if these values are in fact unacceptable.
The grounding electrode impedance is 2.5 ohms, so that is not in question (unless because it seems unrealistically low...)