My company supplied Roof Heating Mats (for snow melting) on a project,
Backgound:
Heaters are constructed of a Thin-Film Polyethylene encapsulating a pair of flat bus-wires. Between the flat bus-wires is a Printed Conductive ink. The heaters produce heat by voltage flowing through the resistive ink and generating heat. The polyethylene is non conductive and terminations are made to the bus-wires then encapsulated in a layer of self-vulcanized insulation. After this the heaters are then sandwiched between two layers of EPDM and the edges are heat sealed to make a waterproof mat with a cold lead sticking out for power.
Heaters are 208 vac rated and installed on an EPDM Roof with adhesive.
Electrical Contractor (EC) noticed that when the mats are wet, and if touched while holding a guard rail, there is definitely a flow of electricity. When a meter is used, it is measuring 110 vac to ground on the outside of the mat (a t-stat is breaking one hot leg of the circuit when not calling for heat). When the T-stat calls for heat, the voltage to ground drops by 50% to 55 Vac.
Manufacturer visited site and felt that there was a manufacturing defect. MFG then sent a whole new set of mats. The originals were taken out and replaced by the new set. The same thing is happening again. This leads me to believe that the mats may not be the cause (These mats are installed in thousands of applications) with zero problems).
The EC did say that they were using the T-stat to break two hot legs from two Circuit breakers. I advised him not to do this.
In the meantime, I have sent a new mat from another manufacturer to the site to see if we get the same leakage, which will rule out the mats and point directly to the building, wiring etc.
Any thoughts on why ground leakage is occurring? I am doubtful it is being caused by the heater mats.
Backgound:
Heaters are constructed of a Thin-Film Polyethylene encapsulating a pair of flat bus-wires. Between the flat bus-wires is a Printed Conductive ink. The heaters produce heat by voltage flowing through the resistive ink and generating heat. The polyethylene is non conductive and terminations are made to the bus-wires then encapsulated in a layer of self-vulcanized insulation. After this the heaters are then sandwiched between two layers of EPDM and the edges are heat sealed to make a waterproof mat with a cold lead sticking out for power.
Heaters are 208 vac rated and installed on an EPDM Roof with adhesive.
Electrical Contractor (EC) noticed that when the mats are wet, and if touched while holding a guard rail, there is definitely a flow of electricity. When a meter is used, it is measuring 110 vac to ground on the outside of the mat (a t-stat is breaking one hot leg of the circuit when not calling for heat). When the T-stat calls for heat, the voltage to ground drops by 50% to 55 Vac.
Manufacturer visited site and felt that there was a manufacturing defect. MFG then sent a whole new set of mats. The originals were taken out and replaced by the new set. The same thing is happening again. This leads me to believe that the mats may not be the cause (These mats are installed in thousands of applications) with zero problems).
The EC did say that they were using the T-stat to break two hot legs from two Circuit breakers. I advised him not to do this.
In the meantime, I have sent a new mat from another manufacturer to the site to see if we get the same leakage, which will rule out the mats and point directly to the building, wiring etc.
Any thoughts on why ground leakage is occurring? I am doubtful it is being caused by the heater mats.