TwoBlocked
Senior Member
- Location
- Bradford County, PA
- Occupation
- Industrial Electrician
Could this be an ungrounded system? Check voltage between the neutral and ground at an outlet.
Did not measure current readings from mat to ground, too low as the GFEPD Circuit Breaker would trip in excess of 30 ma.
Manufacturer recommended controls that open both legs of the 208 vac circuit when not calling for heat, and also switching the GFEPD CB's to standard CB's, since voltage to ground when energized is less than 50 v.
I need to check NEC code for this application to see if GFEPD is required for portable snow mats.
I think I am leaning toward some sort of capacitance occuring. If this is the case, is there any way to eliminate this phenomenon?
I would feel real nervous about switching out the GF protection for a standard breaker.
I think that is pretty much a code requirement 426.28
If not, you can make a coil of wire with ten, 100 or 1000 turns to increase its sensitivity.If you have a clamp meter that is sensitive enough to measure currents less than 30 mA, ...
Both manufacturers are telling me that they do not need GFEPD since their equipment is not "fixed", it is "portable". This is a gray area that needs to be defined.I would feel real nervous about switching out the GF protection for a standard breaker.
I think that is pretty much a code requirement 426.28
Grounded only on one side. We took readings from both sides of mat. Same resultDo you know if both the top and bottom of the heating elements are covered by a grounded conductor?
These mats are installed with adhesive and they are considered portable?Both manufacturers are telling me that they do not need GFEPD since their equipment is not "fixed", it is "portable". This is a gray area that needs to be defined.
Grounded only on one side. We took readings from both sides of mat. Same result
Both manufacturers are telling me that they do not need GFEPD since their equipment is not "fixed", it is "portable". This is a gray area that needs to be defined.
Grounded only on one side. We took readings from both sides of mat. Same result
These mats are installed with adhesive and they are considered portable?
The manufacturer bonds a ground shield onto one side of the heater film. This ground shield is then connected to a ground wire that is part of the power cord.What do you mean 'grounded one side only'? Do the mats include a grounded conductive layer?
The manufacturer bonds a ground shield onto one side of the heater film. This ground shield is then connected to a ground wire that is part of the power cord.
Built exactly like the ones sold online to homeowners.These mats are installed with adhesive and they are considered portable?