Question I have two 4000amp main switchboards each at 480 volts 3 phase .
I have a tie breaker common to both and each is fed from separate utility transformers . When installing the grounding electrode conductor is two separate grounding electrode conductors required one to each service or can one be run to just one switchboard if the ground bars are common to each switchboard and tie breaker .
When grounding electrode conductor is attached to one or both ?
Is it attached to main breaker section or any section close to bonding jumper ground bar or in any location in switchboards ?
I have a tie breaker common to both and each is fed from separate utility transformers . When installing the grounding electrode conductor is two separate grounding electrode conductors required one to each service or can one be run to just one switchboard if the ground bars are common to each switchboard and tie breaker .
When grounding electrode conductor is attached to one or both ?
Is it attached to main breaker section or any section close to bonding jumper ground bar or in any location in switchboards ?