Ground Potential Rise

Status
Not open for further replies.

mbrooke

Batteries Included
Location
United States
Occupation
Technician
I came across this article which talks about ground potential rise from having unbonded grounding electrodes. Its very eye opening and I wish Mike Holt would do a new letter or a you Tube video on CATV bonding. I know there are many misconceptions about this. At my own home for example the CATV has its own ground rod...


http://electrical-engineering-portal.com/ground-potential-rise-in-your-home


what do others think about this article? Right from an electrical theory standpoint?
 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
I have the attention span of a gnat so wading through all that text for about three minutes was about all I could stand.

If I understood correctly the point of the article is that driving extra ground rods is a bad idea, and you are making things worse if you add extra ground rods that don't tie back to the main service. If that is correct then I agree.
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
I have the attention span of a gnat so wading through all that text for about three minutes was about all I could stand.

If I understood correctly the point of the article is that driving extra ground rods is a bad idea, and you are making things worse if you add extra ground rods that don't tie back to the main service. If that is correct then I agree.

Yes- nice synopsis :thumbsup:
 

kwired

Electron manager
Location
NE Nebraska
I came across this article which talks about ground potential rise from having unbonded grounding electrodes. Its very eye opening and I wish Mike Holt would do a new letter or a you Tube video on CATV bonding. I know there are many misconceptions about this. At my own home for example the CATV has its own ground rod...


http://electrical-engineering-portal.com/ground-potential-rise-in-your-home


what do others think about this article? Right from an electrical theory standpoint?
Theory is mostly accurate.

NEC does require bonding CATV to electrical system, as well as other systems. Had this requirement even before the intersystem bonding terminal was added.

You can drive all the rods you want for other systems if that makes you feel good - but they also all need to be bonded together.

Even when all such systems are bonded, the more direct the lightning strike is the more likely you have temporary rise in voltage in some instances or even certain portions of a premises.
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
Theory is mostly accurate.

NEC does require bonding CATV to electrical system, as well as other systems. Had this requirement even before the intersystem bonding terminal was added.

You can drive all the rods you want for other systems if that makes you feel good - but they also all need to be bonded together.

Even when all such systems are bonded, the more direct the lightning strike is the more likely you have temporary rise in voltage in some instances or even certain portions of a premises.

I'd imagine- I remember mike saying that the frequency pulse of lightning is so high that even a few feet of #6 will exhibit significant impedance.

Xl=2piFL
 

grich

Senior Member
Location
MP89.5, Mason City Subdivision
Occupation
Broadcast Engineer
...At my own home for example the CATV has its own ground rod...

Around here, they don't even bother with that, let alone connect to the ISBT. :(

One of my radio station clients added cable internet in between my usual visits. The CATV tech mounted his first splitter 3 feet from the main ground bar. He left it float, and by the time I discovered it, a surge roared in and took out the cable modem, router and one of the ethernet switches. What a mess.
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
Around here, they don't even bother with that, let alone connect to the ISBT. :(

One of my radio station clients added cable internet in between my usual visits. The CATV tech mounted his first splitter 3 feet from the main ground bar. He left it float, and by the time I discovered it, a surge roared in and took out the cable modem, router and one of the ethernet switches. What a mess.

Bonding is more important than grounding. In fact article 250 is mostly around bonding, not grounding. Grounding has little if anything to do with people and property protection at 600 volts and under.
 

Sahib

Senior Member
Location
India
Grounding has little if anything to do with people and property protection at 600 volts and under.
1)Grounding dissipates surge energy lest it should do harm.
2)In case of Mv to LV accidental contact, grounding on LV side limits ground potential rise.
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
1)Grounding dissipates surge energy lest it should do harm.
2)In case of Mv to LV accidental contact, grounding on LV side limits ground potential rise.

Thats a good point- but the ground is only to prevent the voltage of the bonding system as a whole from being overly excessive relative to earth. Ie, reducing the possibility of side flashes and arcing of the bonding system to earth. Even with a good ground it can still rise to thousands of volts when measured to earth just 6 feet away from the ground rod, and as such its the equal potential effect that keeps everything safe.
 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
1)Grounding dissipates surge energy lest it should do harm.

If that were true why would anybody spend money on surge protectors?

2)In case of Mv to LV accidental contact, grounding on LV side limits ground potential rise.

How does it do that? I know that grounding stabilizes voltages to ground in a normally operating system, but when the wires cross things still go boom.
 

Sahib

Senior Member
Location
India
If that were true why would anybody spend money on surge protectors?

Answer : Without ground connection, a surge arrestor does not work.


How does it do that? I know that grounding stabilizes voltages to ground in a normally operating system, but when the wires cross things still go boom.
Answer: Suppose ground resistance is zero. Consider 120V, Singe phase line with neutral grounded. Since ground resistance is zero, no matter how large a current flows through neutral to ground, the ground potential does not rise. Now Suppose a MV line contacts the 120V single phase line. A large short circuit current flows via phase, neutral and ground. But since ground resistance is zero, there is no rise in ground potential and the single phase line remains at 120V. In real situation also, there will be only a little rise above 120V if the ground resistance is close to zero.
 
Last edited:

kwired

Electron manager
Location
NE Nebraska
Answer: Suppose ground resistance is zero. Consider 120V, Singe phase line with neutral grounded. Since ground resistance is zero, no matter how large a current flows through neutral to ground, the ground potential does not rise. Now Suppose a MV line contacts the 120V single phase line. A large short circuit current flows via phase, neutral and ground. But since ground resistance is zero, there is no rise in ground potential and the single phase line remains at 120V. In real situation also, there will be only a little rise above 120V if the ground resistance is close to zero.

Ground is ground AKA the earth. Grounding electrodes always have some resistance, so will the GEC. 120 volts applied to GES with 10 ohm resistance carries 12 amps.

7200 volts applied to 10 ohm GES carries 720 amps.

Voltage "zones" around the electrode are much larger with 120 volts applied then with 7200 volts applied.

Few years ago a local rural POCO had an underground 34.5 kVA that had a failure. They repaired it, for whatever reason their splice method failed when they energized it. It sent a surge down a nearby wire fence, arced across to telephone pedestal(s) near fence. There was damages in many buildings within a couple miles or so - all coming into facilities via telephone lines. Ground rod wasn't going to stop that, AFAIK most the telephone pedestals do ordinarily have a ground rod connected to them. I believe there was a couple grass fires associated with that incident as well.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
If that were true why would anybody spend money on surge protectors?

How does it do that? I know that grounding stabilizes voltages to ground in a normally operating system, but when the wires cross things still go boom.
There's a big difference between line-to-line surges and line-to-earth surges.
 

Sahib

Senior Member
Location
India
Few years ago a local rural POCO had an underground 34.5 kVA that had a failure. They repaired it, for whatever reason their splice method failed when they energized it. It sent a surge down a nearby wire fence, arced across to telephone pedestal(s) near fence. There was damages in many buildings within a couple miles or so - all coming into facilities via telephone lines. Ground rod wasn't going to stop that, AFAIK most the telephone pedestals do ordinarily have a ground rod connected to them. I believe there was a couple grass fires associated with that incident as well.
The ground resistance might be too high to prevent operation of upstream fuses to have caused such damages. I do not think any other reason..........
 

Sahib

Senior Member
Location
India
kwired: I also bet it happened in rural area; not in densely populated urban area where multigrounded neutral ground resistance is very low.
 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
Answer: Suppose ground resistance is zero. Consider 120V, Singe phase line with neutral grounded. Since ground resistance is zero, no matter how large a current flows through neutral to ground, the ground potential does not rise. Now Suppose a MV line contacts the 120V single phase line. A large short circuit current flows via phase, neutral and ground. But since ground resistance is zero, there is no rise in ground potential and the single phase line remains at 120V. In real situation also, there will be only a little rise above 120V if the ground resistance is close to zero.
I don't think what you are saying is possible.
 

romex jockey

Senior Member
Location
Vermont
Occupation
electrician
Bonding is more important than grounding. In fact article 250 is mostly around bonding, not grounding. Grounding has little if anything to do with people and property protection at 600 volts and under.

Exactly the jist of the article's reference to GPR

>>>>

So it is perfectly possible for an AC or signal wire to have 5 kV or more between its two ends, for the short time that the lightning current lasts.

That nanosecond of GPR is far less damaging if the entire residence assumes 1,000,000 volts

VS. 1,000,000 volts on one end, 500,000 volts on the other, which is FAR more damaging.

One can even read this theory into past code cycles. Remember when we didn't bond gas lines? The gas guys would have conniptions....then it evolved to 'within 6' , along with a flashover rationale. , these days we either bond the gas lines or fail inspections.


~RJ~
 

kwired

Electron manager
Location
NE Nebraska
The ground resistance might be too high to prevent operation of upstream fuses to have caused such damages. I do not think any other reason..........
Don't know all details of what happened, would guess overcurrent protection did function maybe just not fast enough.

kwired: I also bet it happened in rural area; not in densely populated urban area where multigrounded neutral ground resistance is very low.
It was in rural area, was also within 1 mile of the substation it was supplied from. After about a mile the line transitions to overhead conductors. This substation is a major hub for the region so to speak. Everyone within 30-50 miles of it is likely being powered through it in one way or another most of the time. The faulted line I mentioned just happened to be just one of the more localized lines leaving the substation.
 