Dennis Alwon;1011198
As far as the GEC to the water pipe it must be connected within 5' of where it enters the house but I don't belive it would be a violation to connect to the water line before it enters the house.
[/QUOTE said:
250.52 Interior connections cannot be made more than 5' from where the water pipe enters the building. Nothing in there regarding the location of exterior connections.