federicop
New User
- Location
- caracas, venezuela
- Occupation
- project consultant
Is there a minimum ground resistance value for fire pump controllers using soft starters? I recently asked the supplier of a controller we are installing and he answered they don't have a value. I'm using the NFPA 70 value of 25 ohm minimum. Peer specialists have advised 5 ohm or less for equipment using electronic sensitive equipment. Thanks