We are working on a project involving the replacement of a pump control panel located in a remote vault. The load is quite small; about 15 amps at 480V 3-phase with a feeder breaker rated for 30A in the main building. The run is very long so the installed conductors have been upsized for voltage drop. Installation is mid 80's. The feeder consists of 3-#1/0 and 1-#2 ground. Aluminum wire type USE XLPE (USE only, not USE-2 or dual ratings)
We are trying to reuse the existing conductors and are checking their ratings and voltage drop.
Regarding the voltage drop, a 30A feeder would have needed #8 with a #8 ground (aluminum). Upsizing the phase conductors to 1/0 would have required a #1/0 ground due to 250.122.B. Therefore, it appears the ground is undersized.
Possible solution:
Since we are putting in a new pump control panel, we have the ability to customize the panel. The plan would be to change the main feeder breaker to a 50A breaker (instead of 30A) and have a 50A breaker main disconnect in the pump panel. The 50A feed would initially need #4 phase and #10 ground (aluminum). With that being the starting point, looking at the load of 15 amps, the #4 would still need upsized. Therefore, they have been upsized from #4 to #1/0. Checking the ground, the new ground would only need to be a #4 which the installed #2 would just be an improvement.
Here is the math for 50A feeder: circular mills:
(new conductors/base conductors) x base ground.
(105600/41740) x 10380 = 26261 CM for new ground = installed #2 meets this.
Does this approach appear viable and I guess my confusion is why with the lower ampacity (30A) VD correction a larger ground is required, but if I increase the circuit ampacity (50A), the VD corrected ground is smaller?
We are trying to reuse the existing conductors and are checking their ratings and voltage drop.
Regarding the voltage drop, a 30A feeder would have needed #8 with a #8 ground (aluminum). Upsizing the phase conductors to 1/0 would have required a #1/0 ground due to 250.122.B. Therefore, it appears the ground is undersized.
Possible solution:
Since we are putting in a new pump control panel, we have the ability to customize the panel. The plan would be to change the main feeder breaker to a 50A breaker (instead of 30A) and have a 50A breaker main disconnect in the pump panel. The 50A feed would initially need #4 phase and #10 ground (aluminum). With that being the starting point, looking at the load of 15 amps, the #4 would still need upsized. Therefore, they have been upsized from #4 to #1/0. Checking the ground, the new ground would only need to be a #4 which the installed #2 would just be an improvement.
Here is the math for 50A feeder: circular mills:
(new conductors/base conductors) x base ground.
(105600/41740) x 10380 = 26261 CM for new ground = installed #2 meets this.
Does this approach appear viable and I guess my confusion is why with the lower ampacity (30A) VD correction a larger ground is required, but if I increase the circuit ampacity (50A), the VD corrected ground is smaller?