I have designed/built hundreds of them in the telecom industry, you weld to the ring. As stated it is a ring with no beginning or end, well until your Wife's Lawyer gets through with you.exothermal weld?? ,,,couldnt you just exit the load center encircle the building
and connect the ring with a direct burial bug connector..?
exothermal weld?? ,,,couldnt you just exit the load center encircle the building
and connect the ring with a direct burial bug connector..?
Bob I agree with you 100%, but in the Telecom sector or any facility that depends on the GES, there is no better method for a worry-free connection assuming it is done properly and the connections tested with a hammer. For Ufer Burndy Hy-Ground compression is fine, but when it comes to dirt, weld it and forget it. Heck I even specify the GEC connection to the office principle ground bar be welded.As much as I am a Cadweld fan I want to make clear the NEC does not require it for a grounding ring. Any connector listed for the purpose is acceptable to the NEC.
I agree,, that was my orignal point to my question,,, so basically according to code,,, I can exit the main panel encircle the building and dead end the wire outside the building as long as i meet the code requirements to size of wire , depth , and length or run ,,, right?
you could start and stop in the panel per the NEC