I apologize for chiming back in late on this but the past few weeks have been hectic.
I was actually able to make it out to the site to inspect the existing building that is being expanded only to find that there does not appear to be an existing ground ring or really any grounding electrode for that matter. We were told there was an existing ground ring but when contractor started excavating around building there was no ground ring to be found, so I apologize for stating that assumption.
Here is what I did find:
As I mentioned earlier this building houses two 480V MCC's which are fed from as double ended substation in a building about 100ft or so away. I found that the ductbanks that feed these MCC's have a 4/0 ground wire run in the ductbank that come up through the concrete slab and attached to the ground bus in the MCC. The 4/0 ground wire in ductbank runs back to the substation building where I know for a fact there is an extensive grounding system with multiple ground rods, rings, etc... The only issue however is that this ductbank goes through manholes so I'm not sure that that this ground wire is continuous all the way back through the manholes (under investigation). So it appears that the only grounding this room has is the ground wire coming through the existing ductbanks that connect to the MCC ground buses. These ductbanks are being replaced, but the ground wire will also be replaced and re-run as well.
Inside the room there are 3 panels and a dry type that are all connected to a ground bar mounted on the wall. the ground bar from what I could tell was not connected to the physical ground at any point but rather had a ground wire run in a conduit that went back and connected to the ground bus in one of the MCC's.
So I guess in seeing this my other question becomes weather or not the existing grounding electrodes at the adjacent substation building (100ft) away can be utilized as the grounding electrodes for the building where the MCC's are via the grounds in the ductbanks? Is there a limit on how far away the grounding electrodes can be.
With all that said we are still going to expand the existing buildings that the MCC's are in and need to specify grounding for the expansion. Obviously as others have mentioned, the easiest thing to do is to utilize a CEE in the new foundation. However given this new information on the existing buildings grounding is there a need or requirement to tie the expansion buildings ground into the exiting buildings ground via the MCC ground bus?
This thread has been helpful and the one thing I did learn was the requirement in 250.50 to use all available grounding electrodes weather they be CEE's, building steel, water pipes, etc... To what distance does this requirement apply? For instance if there are water pipes running in the vicinity of the building are they required to be utilized. Say the pipe are 50ft or even 75ft away, are they required to be used? Is there a distance/depth requirement for having to use a water pipe if it is present?
Lastly assuming that I only need to use a CEE to meet the minimum requirement, is it a good idea to install additional grounding electrodes or rings around the expansion? I know the NEC dictates the minimum and is not a design guide, but most industrial designs I see seem to utilize a ground ring which is tied into the rebar in the foundation. Do you think it would be wise to try to somehow tie into the exiting buildings foundation rebar once the wall is removed an there is possible rebar that is exposed or can be made exposed for connection?