Ground Ring

Merry Christmas
Status
Not open for further replies.

svaurez

Member
Location
California
I read on this forum that a ground ring electrode must encircle the ENTIRE building.Was this the NEC's intention or is the ground ring just 20' of #2 buried in the dirt.
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: Ground Ring

250.52(A)(4) Ground Ring. A ground ring encircling the building or structure, in direct contact with the earth, consisting of at least 6.0 m (20 ft) of bare copper conductor not smaller than 2 AWG.
 

svaurez

Member
Location
California
Re: Ground Ring

I have trouble believing they want the entire building surrounded with #2.They allow 10' of copper water pipe,an 8' ground rod,and a 2 by 2 copper plate as electrodes.20' of #2 will outclass any of these.

[ January 04, 2004, 10:46 AM: Message edited by: svaurez ]
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: Ground Ring

The code requires that the ground ring encircle the building or structure. I agree that 20' of copper in a ditch should perform as well as a 20' ground ring, but the code does not list 20' of copper in a ditch as a grounding electrode.
Don
 

earlydean

Senior Member
Re: Ground Ring

The only place I have seen ground rings installed is around transformer pads. As is noted here, they would be too expensive to choose for most buildings. Maybe somebody should test 20 feet of #2 in the dirt, 40 inches down and submit the results to NFPA for inclusion in the NEC. That's how Ufer did it.
Nah, nobody will do that, there is no money in it.
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: Ground Ring

Earl many of the large buildings we do have ground rings specified on the plans

Typically 4/0 bare around the building with taps of 4/0 to 2 AWG into building columns and footing rebars.

Most of these will exceed 1000' feet in length, some have been much longer than that, the last one I worked on was getting near 2500' of 4/0 just to get around the building.
 

bennie

Esteemed Member
Re: Ground Ring

The purpose of the ground ring is to create a low impedance ground plane. The impedance to earth is secondary.

The building steel will be closer to the same voltage, to earth, at all locations when connected to a low impedance ground plane.

When the equipment is multi point grounded there will not be a high common mode voltage.
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Re: Ground Ring

Earlydean: the test by Ufer was with 4 AWG in concrete. I have a copy of his 1960 IEEE article. If he did a study with 2 AWG in dirt could you send me the article year and date, I will order it from the IEEE.
 

brian john

Senior Member
Location
Leesburg, VA
Re: Ground Ring

Dean:

there are so many variables in installing and testing ground electrode that a large test would need to be completed to achieve and usable data, depths, locations, time of year, variable soil conditions, corrosion/detrition over time. A large ring can over come some of these variables and makes the installation of lightning protection easier, for the connection of down conductors.
 

svaurez

Member
Location
California
Re: Ground Ring

One more quick question.

Does the ground ring have to be spliced to form a complete circle with a cadweld,or can the two ends just lay in the trench overlapping each other?
 

bennie

Esteemed Member
Re: Ground Ring

A complete ring is a must. The principal is to have the same resistance between any two nodes regardless of where the connections are made.

Cadweld the ends with a butt splice.
 

friebel

Senior Member
Location
Pennsville, N.J.
Re: Ground Ring

To: svaurez;don_resqcapt19;dereck;tom baker;
I have been reading with interest your comments about a grounding ring around a building.
I realize the NEC allows you to have a ground-ring around a building. This has been my experience in industry with a ground-ring, which I would like to see removed from the NEC, and for this reason.
Many times when an excavating crew comes in with their front-end loader to remove some soil, they inadvertenly will break the ground wire, which as you know can be a potentially serious problem. We have gone extensively with the Ufer grounding system, along with the Main water line, and a driven ground for our grounding for a building.
I hope that you may see the concerns that I have with a ground-ring around a building that is not protected, and can be very easily broken, when excavating.
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: Ground Ring

I do not think there is a chance that you will see ground rings go away.

I have seen the problem you speak of as I have been called into repair broken ground rings from excavators.

The jobs I have worked specify a marking ribbon above the ground ring but when an excavator comes in with a 4' x 5' x 6' bucket it all gets picked up in one scoop. :roll:
 

bennie

Esteemed Member
Re: Ground Ring

The ground ring should be a minimum of 30 inches below finished grade. Breaking the continuity of the ring may have some effect on the performance of sensitive equipment but the resistance of the earth connection should not be compromised.

The ground ring is likely not the only electrode in the system.

A ring establishes both a building ground and an equipment ground.
 

bennie

Esteemed Member
Re: Ground Ring

Pierre: I should have stated; The ground ring provides a ground plane for the sensitive equipment.

The ring provides an earth connection for the electrical system.
 