Ground Ring

Merry Christmas
Status
Not open for further replies.

dereckbc

Moderator
Staff member
Location
Plano, TX
Re: Ground Ring

Pierre, I have worked in the Telecom industry most of my career, and here is my two cents worth on ground rings. They are most beneficial if used in conjunction with a lightning protection sub-system to minimize step-potential differences inside a protected facility.

In facilities like a phone office or data centers you have outside plant cables (AC, copper, fiber, coax, etc.) entering at different locations along the outside walls. With a ring in place it makes it very easy to obtain access where the cables enter to facilitate installation of SPD's and other GE connections.

I do not really care what the impedance is to ground unless I am under government contract to provide a target. But in my experience a ring most of the time provides 5 ohm's or less. Personally I do not use the minimum number 2 AWG but rather a 2/0 with welds for all connections.
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Re: Ground Ring

Remember folks a ground ring is a performance ground system, as opposed to the prescriptive grounds (ground rod) we normally see. This type of ground is installed for some specific purpose. To me its the differerence between a cup of coffee (prescriptive) and a double tall skinny latte (performance). Both do the job but the with the latte it costs a lot more.
 

hurk27

Senior Member
Re: Ground Ring

I agree Tom
The ring electrode is the start of a fairaday cage and when all the connection's to the air terminals and the ridge conductor is compleat it would be about the closes thing you could get to a fairaday cage.
 