Ground Riser

Status
Not open for further replies.

mstrlucky74

Senior Member
Location
NJ
Anyone know what you would use to tap off the # 500 vertical grounding conductor to go to the ground bar? T Tap?
 

Attachments

  • Capture.JPG
    Capture.JPG
    122.4 KB · Views: 2

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Yes that is what I was thinking for a crimp connection. For a mechanical connection I would use a IPC type tap.

(IPC)%20Insulation%20Piercing%20(Dual%20Rated).JPG
 

tom baker

First Chief Moderator
Staff member
If this is a GEC and the riser is EMT, the ends of the EMT need to be bonded to the 500 KCML See 250.68 (E), Since the dwg shows transformer I am pretty sure this is a GEC. You would be much better off using SCH 80 PVC for the conduit. Your bonding jumper for the ends of the EMT has to be 500 KCML. The size for the common grounding electrode conductor is not smaller than 3/0
250.30 (A)(6). At the end of that section is the requirements for the tap conductor connection. Not sure why 500 KCML is being used but there may be an engineering reason
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
You're correct, this is actually a common grounding riser under 250.30(A)(6). A grounding hub can be used on the EMT to bond it directly to the riser. Not sure why anyone would spec 500 kcmil when #3/0 is all that's required.
 