Re: ground rod - 0 ohms
I will try to help you out as I have done a lot of GES and lightning protection for telephone companies requiring 5 ohms or less.
Seriously doubt anyone is going to be willing to pay to get down to 5-ohms or less unless you just happen to be lucky and have good soil. Achieving the 5 ohms or less take engineering, planning and soil test, it just does not happen on it's own.
OK now to answer your question. There are two methods of measuring ground resistance, one semi accurate, the other is ball park.
The semi accurate method is known as "Dead Fall Of Potential" method using either a 3-point or 4-point system and an instrument called a Meggar. The down side is this. For the test to be accurate, the 3 or 4 points has to be at least 6 times as large as the area of the GES, preferable 10 times. So just for a two rod system spaced say 20-feet apart, the two furthest test points would need to be 120 to 200 -feet apart from one another. To complicate things, the test must be performed several times moving the probes on a different plane. After all the measurements are completed you then average the reading to get the mean average. I think you can see the problem real quick. Lets say your building is 100 x 100 feet, or diagonally 140 feet. 140 times 10 is 1400 feet. That means you need cable at 1400, and another at 600 feet to perform the test. Couple that with multiple test. Where are you going to find that much space to string those cable across neighborhoods multiple times.
The other method is easy. You use a clamp on ground tester. You clamp one of the rods, read it and walk away your done. Problem is it is not accurate because of the way the meter works. It takes the resistance of the rod under test and adds it to the series of the rest of the rods in parallel. Not much of a problem though, because whatever it reads you actual impedance is really lower than it reads.