Ground rod at non-service disconnect switch?

Status
Not open for further replies.

rrc14

Member
Location
Anchorage, AK
Occupation
Engineer
Working on a project where we are installing a 150A, 480V, 3-phase feeder, (3 conductors and a ground) from a MCC over to another building. This feeder is being terminated to a safety disconnect switch mounted on the exterior wall of the building. The question that I have is does this safety disconnect switch need to be tied in to a ground rod at the building? It is not a separately derived power source. Looking over Article 250 in NEC and it is still not clear to me yet. Any comments would be appreciated. Thanks,
 
Yes, it is the only feeder for the building. The feeder provides electricity to a 480V-120V/208Y step-down transformer, which then feeds a panelboard. The secondary of the step-down transformer is grounded to a ground rod.

I was unclear if the 480V feeder (3 conductors & ground) needed to be grouded to a ground rod since it wasn't a separtely derived system.
 
If an EGC is run with the feeders from the MCC than what is the purpose for providing a seperate grounding electrode at the building disconnect. I know the code requires it, but what purpose does this serve?

I know ground fault current flowing through ground will not be large enough to trip an OCPD so is this grounding electrode to help eliminate touch potential?
 
If an EGC is run with the feeders from the MCC than what is the purpose for providing a seperate grounding electrode at the building disconnect. I know the code requires it, but what purpose does this serve?
Just like at a service the grounding electrode is to provide some protection from lightning and contact with higher voltage systems.
I know ground fault current flowing through ground will not be large enough to trip an OCPD so is this grounding electrode to help eliminate touch potential?
A grounding electrode does little to eliminate step and touch potentials.
 
I was unclear if the 480V feeder (3 conductors & ground) needed to be grouded to a ground rod since it wasn't a separtely derived system.
It is not the feeder that brings into play the requirement for a ground rod. It is the building itself. Each structure that has a source of electrical power must have a grounding electrode.
 
If an EGC is run with the feeders from the MCC than what is the purpose for providing a seperate grounding electrode at the building disconnect. I know the code requires it, but what purpose does this serve?

I know ground fault current flowing through ground will not be large enough to trip an OCPD so is this grounding electrode to help eliminate touch potential?

Lightning.
 