250.50 requires a Grounding Electrode and Grounding Electrode Conductor at each structure. I suppose we could argue until Christmas whether an Optional Standby Generator is a separate ?structure.? If you poured a concrete slab which contained 20 feet of reinforcing rods and put your generator on top of it, then you have built a separate structure and you are required to have a GEC and Grounding Electrode at this structure. It all depends on what your definition of is is.
By my definition, a Permanently Installed Generator installed in a separate location is a separate structure. What the AHJ says is another matter.
As far as Generator design, how do manufactures know how you will install your generator? A separately derived system clearly requires a GEC and GE at the generator according to 250.30. As I have said in an earlier post, many generator manufacturers have not kept their designs up to date with changes in the NEC in my opinion.
By installing a GEC and GE at the Generator, no matter whether it is a Separately Derived System or not, connection to the earth should limit the voltage imposed by lightning, line surges, or unintentional contact with higher-voltage lines and will stabilize the voltage to earth during normal operation.