MKinnes said:It is above ground. The message on got on my voice mail was that he would like to see one driven to help the ground fault to open up. Also he is a new inspector and I'd rather not pick a fight with him if I don't have to
Absolutely true. Consider this: Take a 120 volt source, and use it to push current through a ground rod that has a ground resistance of 25 ohms. What current do you get? 120/25 is 4.8 amps. Ask the inspector how that is going to help trip whatever size breaker is feeding the pool?s electrical equipment. To trip a breaker fast enough to prevent an injury to a person, you need a current many times the rating of the breaker. That is the function of the Equipment Grounding Conductor. It has a resistance well under a tenth of an ohm, and will result in a fault current over 1000 amps. An extra 4.8 amps going through a ground rod will not have any influence at all.roger said:Well, with that statement, he shows that he needs some grounding classes, the ground rod will play no part of operating or opening (at our voltages) an OCPD in a fault.
winnie said:I absolutely agree that this ground rod is not required, however:
With a proper EGC and required bonding, this ground rod is essentially irrelevant, but a normal 8' ground rod in soil will certainly couple enough current back to the source to be able to trip a GFCI breaker. Even a 1000 ohm resistance to ground would trip a GFCI.
-Jon
MKinnes said:It is above ground. The message on got on my voice mail was that he would like to see one driven to help the ground fault to open up.
True, but the 1000+ amps flowing through the EGC at the same time might also ?help? trip the GFCI breaker.winnie said:. . . but a normal 8' ground rod in soil will certainly couple enough current back to the source to be able to trip a GFCI breaker. Even a 1000 ohm resistance to ground would trip a GFCI.
And recommend to him/her that they attend one of Mike Holt's GvB seminars if the opportunity arises! :wink:dcspector said:My thoughts are as mentioned..... A NEW INSPECTOR.....give Him or Her a break and educate them.
earshavewalls said:If you installed the ground rod, you would then be obliged to tie it in to the house GEC. This would mean more trenching, etc.