190729-1652 EDT
I have a grounding electrode for my home that can be defined as 150 feet of 1.25" copper tubing. This is my water supply from the street. My home has no ground rod or other grounding electrode. The water pipe is it.
The pole transformer has a ground rod adjacent to the pole. This is 70 to 80 feet from my water entry point, which is also where my main panel is.
Our primary supply is an ungrounded delta, grounded only at the substation. I have one neighbor sharing this transformer. There is no neutral sharing from one neighbor to another, except for those that share a transformer.
So my one neighbor and I share grounding thru the earth and power wiring. We don't share the same water main.
To a large extent I can define my water line as remote earth.
My power transformer ground rod has no effect on my experiment because it is away from my experiment in an opposite location 150 feet or so from my experiment location.
Near the road where my water line enters the property I drove into the earth 9 feet worth of 1/2" copper coated steel ground rod about 25 feet from the water line.
With 120 V applied to the experiment rod current flow was 3.5 A. This is a rod to my defined remote earth earth impedance of about 34 ohms. The water line is more than 6 feet below the earth surface. Possibly 8 feet.
Thru the magnetic field I can detect where the water line is located.
The surface potential gradient was approximately, using eyeball measurement for distance, 99 V to 3 foot radius, 107 V to 6 foot radius.
From the main panel neutral or EGC to a point above the water line the voltage difference was 2 V. My leads were not long enough to measurer from the test ground rod to the point over the water line. This may not make sense, but from the plug into the extension cord that supplied 120 V to the test rod I also had a long EGC wire.
.
I have a grounding electrode for my home that can be defined as 150 feet of 1.25" copper tubing. This is my water supply from the street. My home has no ground rod or other grounding electrode. The water pipe is it.
The pole transformer has a ground rod adjacent to the pole. This is 70 to 80 feet from my water entry point, which is also where my main panel is.
Our primary supply is an ungrounded delta, grounded only at the substation. I have one neighbor sharing this transformer. There is no neutral sharing from one neighbor to another, except for those that share a transformer.
So my one neighbor and I share grounding thru the earth and power wiring. We don't share the same water main.
To a large extent I can define my water line as remote earth.
My power transformer ground rod has no effect on my experiment because it is away from my experiment in an opposite location 150 feet or so from my experiment location.
Near the road where my water line enters the property I drove into the earth 9 feet worth of 1/2" copper coated steel ground rod about 25 feet from the water line.
With 120 V applied to the experiment rod current flow was 3.5 A. This is a rod to my defined remote earth earth impedance of about 34 ohms. The water line is more than 6 feet below the earth surface. Possibly 8 feet.
Thru the magnetic field I can detect where the water line is located.
The surface potential gradient was approximately, using eyeball measurement for distance, 99 V to 3 foot radius, 107 V to 6 foot radius.
From the main panel neutral or EGC to a point above the water line the voltage difference was 2 V. My leads were not long enough to measurer from the test ground rod to the point over the water line. This may not make sense, but from the plug into the extension cord that supplied 120 V to the test rod I also had a long EGC wire.
.