Its function is to make the designer feel better about the design and makes more money for the installer. It does not have much to do with electrical safety at all.We're doing a parking lot where the electrical design shows 8' copper ground rod in every light pole. My questions are:
1. What is the function of this copper ground rod in every light pole? Is good, bad or doesn't matter install this ground rod in terms of electrical safety?
The ground fault path is always thru the EGC. In fact, the code forbids using the earth as a GF path.2. Isn't enough the EGC running with the circuits conductors feeding the light pole providing a ground fault current path to open the circuit in the event of ground fault?
In my understanding the ground rod is not necessary but some expert can clarify this or I'm missing something. Thanks
The code specifically exempts light poles as a structure requiring its own GES. If it required a GES, it would need to have two rods 6 feet apart.