For protection from lightning, you are dealing with a huge number of variables and lots of random chance.
A ground rod at every pole _might_ help conduct a strike into the earth, but keep in mind that lots of the damage is done by the current spreading through the earth. A ground rod might be the path that currents in the earth enter the wiring, exiting at a different ground rod. These earth currents are a big reason that all ground electrodes must be bonded together, and why isolated ground electrodes (eg. separate ground rods for telephone and power) are a very bad idea.
For protection from shock, I'd like to see residual current detection such as @jaggedben suggests. Would probably need to have reliable EGC systems and lower sensitivity that GFCI to maintain safety while avoiding nuisance tripping, because I don't think a class A GFCI would be reliable on an extended outdoor circuit.
Jon
A ground rod at every pole _might_ help conduct a strike into the earth, but keep in mind that lots of the damage is done by the current spreading through the earth. A ground rod might be the path that currents in the earth enter the wiring, exiting at a different ground rod. These earth currents are a big reason that all ground electrodes must be bonded together, and why isolated ground electrodes (eg. separate ground rods for telephone and power) are a very bad idea.
For protection from shock, I'd like to see residual current detection such as @jaggedben suggests. Would probably need to have reliable EGC systems and lower sensitivity that GFCI to maintain safety while avoiding nuisance tripping, because I don't think a class A GFCI would be reliable on an extended outdoor circuit.
Jon