Danny89
- Indian Land
Sunday funday. So to my understanding in a residential setting it is required to install a ground rod for a new sub panel install at the shed building where the panel will be installed. Am I correct?
Here's what I would do.
1) PVC underground dig trench dig it deep enough by referencing burial depth chart.
2) pull in 4 wires to match 50 amp load of new sub panel...(2 hots,neutral, and ecg)from main panel of home to subpanel at shed.
3)drive ground rod in ground 8 feet down til just above grade.
4) don't bond mbj at subpanel. It's already bonded at main panel.
5) run and connect ground from sub panel to ground rod at shed.
6) terminate 4 conductors from main panel to subpanel.(2hot,neutral and egc.)
7) distance is roughly 100 feet away from house to shed.
Let me know what you think. Happy Sunday to all.
Sent from my Moto Z (2) using Tapatalk