You don't have a choice, a grounding electrode is required for the secondary side of this transformer.CCCI said:I'm not looking to add a GE, I do not have anything but a grounding conductor in the feed to the transformer itself.
It is a 480 volt single phase (two hots and a grounding conductor) to 240/120 volt single phase 15 KVA transformer/panel (a combo unit). The only grounds in the transformer is the grounding conductor from the feed to the transformer and the branch circuits that feed out of the panel to the lights and outlets.