D.Rater

Member
A rookie inspector has said that he'll reqire 2 gnd rods; (I doubt that they're on '05 code yet) and it's up to me to prove the resistance. Thoughts?
 
Re: Ground rod ohms

the code requres proof of I believe 25 ohms or less if you cant prove it were required to drive two ground rods.About time the code starts getting enforced. jmho.
 
Re: Ground rod ohms

As stated drive two rods and go home unless you are willing to invest in test equipment, arrange for another inspection, and be there and prove it.

[ January 04, 2006, 08:28 PM: Message edited by: dereckbc ]
 
Re: Ground rod ohms

I don't have 2005, cause we're still on 99 in Ca. unless somethings's finally happened and I havn't heard about it yet.

Does the "code" say that the contractor has to "prove" the 25 or less ohms?

If not, I beleive it's a valid debate as to who has to "prove" anything. Why shouln't it be assumed that the AHJ has the burden instead?

What's easier aside. I don't consider what's easier to be a valid answer to a legitamate question.
 
Re: Ground rod ohms

If this is a new building put in a #4 copper CEE before the footing is poured and forget about the rods altogether.
 
Re: Ground rod ohms

Sam you are right. The contactor does not have to prove anything per se. The contractors installation must meet the 25 ohm standard. How is the contractor to know that it does or does not meet the standard without testing it? Options are contractor buys test equipment to ensure installations are compliant or install two rods.
 
Re: Ground rod ohms

the article is 250.56 and it states that if the resistance is not less than 25 ohms it should be supplemented by a second ground rod thus the burden is on us imho.
 
Re: Ground rod ohms

southernboys most will agree with you about this, then you have some that would stand there and argue with a fence post .
 
Re: Ground rod ohms

Several years ago, the state of WA went around the state and tested several ground rods. Out of all of those tested, not one met 25Ω or less. Now, unless we can prove to the inspector that we have met that threshold, we must pound two rods. It's easier and cheaper to pound the 2nd rod in the ground.
 
Re: Ground rod ohms

Speaking of ground rods and inspections, my friend showed me a neat trick the other day. He had a jar of those flourescent zip ties and no real use for them so he started placing one on each ground rod when they are buried in mulch. The inspector really liked that he didn't have to hunt for the connections. Never hurts to grease the skids a little.

Mark
 
Re: Ground rod ohms

I have also encountered specs that say you must have it tested by an uninterested party, in other words you gotta hire someone to tell you if it's good or not.
 
Re: Ground rod ohms

In my area it is real simple, pay $340 to have it tested and when it fails we get to install 2nd grd rod anyway.

Now lets see "What am I going to do?"

Forget the test it is less expensive to install 2nd rod in the first place. :(
 
Re: Ground rod ohms

The NEC does not place the burden of proof on anyone. It just states the requirement that southerboys#2 cited. Therefore, nothing prevents the inspector from seeing only one rod and asking a question about the ground resistance of that one rod. Also, nothing prevents an inspector from declining to approve an installation without first getting a satisfactory answer to that question.

My only problem would be if a single rod was tested and did show a resistance of 25 ohms or less, and if the test results were to be shown to the inspector, but the inspector says he wants to witness the test and tells the installer to do the test again. I don't know if that ever happens, but I would say that that would be an example of the abuse of authority.
 
Re: Ground rod ohms

Originally posted by paul:
Several years ago, the state of WA went around the state and tested several ground rods. Out of all of those tested, not one met 25Ω or less. Now, unless we can prove to the inspector that we have met that threshold, we must pound two rods. It's easier and cheaper to pound the 2nd rod in the ground.
Same thing here in WI. Drive 2 and call it a day! Of course the better bet is the CEE.
 
Re: Ground rod ohms

IMO the inspector would be within their authority to see the test conducted.

The testers we have do not produce a report, they look like Digital or analog voltmeters.

I am sure there are meters that can produce a report but even at that I think I would be on shaky ground telling the inspector they must accept it.

I look at it the same way I do for a rough wall inspection.

The inspector must be called before the walls are closed so they can see the work, they do not have to take my word for it that I performed the work to code. If I take pictures and then the wall gets closed they may accept the pictures or may say no way.

I have had agreements with inspectors where I could close trenches without inspection if I kept pictures of the work.
 