Ground rod on a subpanel in an attached building

Status
Not open for further replies.

TWControls

Member
Location
United States
While in understand that a ground rod is required on a detached building's subpanel, is there anything that says you cannot put a ground rod on a subpanel that is in the same structure as the main panel? I have a 100 amp sub panel 220V with a separate neutral and ground coming from the main panel. I've always added a ground rod to a subpanel when it was reasonable to install one. My understanding has always been that while not required, it is against code to do it. I'm being told that you can't have a ground rod connected to a subpanel even if you still have an equipment grounding conductor. No code was given to support it but I can't find anything stating either way on this. Does anyone know any code sections stating either way?

Thanks
TW
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
While in understand that a ground rod is required on a detached building's subpanel, is there anything that says you cannot put a ground rod on a subpanel that is in the same structure as the main panel? I have a 100 amp sub panel 220V with a separate neutral and ground coming from the main panel. I've always added a ground rod to a subpanel when it was reasonable to install one. My understanding has always been that while not required, it is against code to do it. I'm being told that you can't have a ground rod connected to a subpanel even if you still have an equipment grounding conductor. No code was given to support it but I can't find anything stating either way on this. Does anyone know any code sections stating either way?

Thanks
TW
Per 250.54 it would be allowed but it would have to isolated from the neutral and basically a waste of materials and labor.

Roger
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
While in understand that a ground rod is required on a detached building's subpanel, is there anything that says you cannot put a ground rod on a subpanel that is in the same structure as the main panel? I have a 100 amp sub panel 220V with a separate neutral and ground coming from the main panel. I've always added a ground rod to a subpanel when it was reasonable to install one. My understanding has always been that while not required, it is against code to do it. I'm being told that you can't have a ground rod connected to a subpanel even if you still have an equipment grounding conductor. No code was given to support it but I can't find anything stating either way on this. Does anyone know any code sections stating either way?

Thanks
TW

Nope, it's permitted and called by the NEC an auxiliary grounding electrode. Roger gave you the code reference 250.54.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
It can also be part of the conventional GES and located at/near a subpanel, but it must then be connected back to the rest of the GES by a conductor that is sized as a ground bonding jumper rather than sized as an EGC.
The open question for me is whether you can share that bonding jumper with the EGC in the same way that you can share the GEC and EGC functions.

Sent from my XT1585 using Tapatalk
 

Smart $

Esteemed Member
Location
Ohio
It can also be part of the conventional GES and located at/near a subpanel, but it must then be connected back to the rest of the GES by a conductor that is sized as a ground bonding jumper rather than sized as an EGC.
The open question for me is whether you can share that bonding jumper with the EGC in the same way that you can share the GEC and EGC functions.
You can, but you must meet all the requirements for both a GEC and an EGC [unspecified 2008 and prior; prohibited 2011 NEC 250.121; permitted 2014 NEC 250.12 Exception], which in part includes running it with the feeder conductors.
 
Last edited:

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I should add that I see no purpose taking it beyond an auxiliary electrode connected via EGC for just a single ground rod.

I agree and 250.54 clearly states that it does not need to be included as part of the building GES.

250.54 Auxiliary Grounding Electrodes. One or moregrounding electrodes shall be permitted to be connected to
the equipment grounding conductors specified in 250.118
and shall not be required to comply with the electrode
bonding requirements of 250.50 or 250.53(C) or the resis-
tance requirements of 250.53(A)(2) Exception, but the
earth shall not be used as an effective ground-fault current
path as specified in 250.4(A)(5) and 250.4(B)(4).

250.50 Grounding Electrode System. All grounding electrodes as described in 250.52(A)(1) through (A)(7) that are
present at each building or structure served shall be bonded
together to form the grounding electrode system
. Where
none of these grounding electrodes exist, one or more of
the grounding electrodes specified in 250.52(A)(4) through
(A)(8) shall be installed and used.
 