I see quite a few post, one rod two rods.
What really is the big deal with today's hammer drills drive two rods and be done with it.
Had a job where the contractor wanted to test his two rods seems they were more than 6 feet apart and the AHJ would not accept the install.
I tried to explain to them that 6 feet is a minimum and most likely makes the tow rods less effective and rod electrodes will have better performance at greater distances. When I quoted the guy to test he decided to drive a 3rd electrode 6 feet from one of the original. Not sure if the AHJ allowed him to use all 3 driven electrodes.
What really is the big deal with today's hammer drills drive two rods and be done with it.
Had a job where the contractor wanted to test his two rods seems they were more than 6 feet apart and the AHJ would not accept the install.
I tried to explain to them that 6 feet is a minimum and most likely makes the tow rods less effective and rod electrodes will have better performance at greater distances. When I quoted the guy to test he decided to drive a 3rd electrode 6 feet from one of the original. Not sure if the AHJ allowed him to use all 3 driven electrodes.