jwjrw
Senior Member
So your area does not use the NC State Electrical Code?
Roger
I didnt know we had a state electrical code. Every county I have worked in require 2. I know meck county has it on the web site or did at one time.
So your area does not use the NC State Electrical Code?
Roger
Even if you have a CEE?
TWO 5/8 ground rods and #4 required by my ahj and several near by.
More clueless inspectors.
Yep did a coffee shop put 20 feet #4 in concrete, 2 ground rods, think it was 1/0 to building steel and water pipe.
Apparently someone thinks so.:roll:You didn't need the rods with a CEE.
#6 is legal but then there is issue with protection. Just easier to run #4
You didn't need the rods with a CEE.
I can only tell you right or wrong here you get 2 ground rods even with a cee.
Can you show me where it says you dont need supplemental rods if you have an cee? Maybe next time Ill try to fight it.![]()
(2) Supplemental Electrode Required. A metal underground water pipe shall be supplemented by an additional electrode of a type specified in 250.52(A)(2) through (A)(8). Where the supplemental electrode is a rod, pipe, or plate type, it shall comply with 250.56. The supplemental electrode shall be permitted to be bonded to the grounding electrode conductor, the grounded service-entrance conductor, the nonflexible grounded service raceway, or any grounded service enclosure.
I can only tell you right or wrong here you get 2 ground rods even with a cee.
Can you show me where it says you dont need supplemental rods if you have an cee? Maybe next time Ill try to fight it.![]()
I can only tell you right or wrong here you get 2 ground rods even with a cee.
Can you show me where it says you dont need supplemental rods if you have an cee? Maybe next time Ill try to fight it.![]()
It's not wrong to do it but it isn't right to require it. If we (us and inspectors) just read the book once in a while we wouldn't be having these issues.
Like alot of electricians I struggle in some areas that I havent got alot of experience in. Looking at plans tells you what to do not why. I am trying hard to learn what I dont know yet. The things I have learned over the years I know and do well. The things I need to learn I hope chatting on here will help with. Thanks guys your a big help.![]()
Many of us do things certain ways because that's the way we were taught. Doesn't mean that those methods are always required or correct. Also the NEC changes every three years so what was applicable yesterday may not be required today. I see this out in the filed quite often. Doing things that are not required because someone was told (incorrectly) that it is required.