I believe this says it all..
neutral earthing
Posted by mukesh on November 29, 2006
Sir,
Why we ground transformer (star side) and Generator?s.
IEEE Std 142-1991 (Green Book) section 1.4.2 states "Numerous advantages are attributed to grounded systems, including greater safety, freedom from excessive system over-voltages that can occur on ungrounded systems during arcing, resonant or near-resonant ground faults, and easier detection and location of ground faults when they do occur." OK, now that we have established why you need to ground the neutral, let's discuss how to ground the neutral. If you effectively ground the neutral, you have just replaced the hazards with ungrounded systems with new hazards in the form of Arc Flash / Blast Hazards. IEEE Std 141-1993 (Red Book)section 7.2.4 states "A safety hazard exists for solidly grounded systems from the severe flash, arc burning, and blast hazard from any phase-to-ground fault." For this reason, IEEE recommends resistance grounding. IEEE Std 142-1991 (Green Book) section 1.4.3 states "The reasons for limiting the current by resistance grounding may be one or more of the following: 1) To reduce burning and melting effects in faulted electric equipment, such as switchgear, transformers, cables, and rotating machines. 2) To reduce mechanical stresses in circuits and appartus carrying fault currents. 3) To reduce electric-shock hazards to personnel caused by stray ground-fault currents in the ground return path. 4) To reduce the arc blast or flash hazard to personnel who may have accidentally caused or who happen to be in close proximity to the ground fault. 5) To reduce the momentary line-voltage dip occasioned by the clearing of a ground fault. 6) To secure control of transient over-voltages while at the same time avoiding the shutdown of a faulty circuit on the occurrence of the first ground fault (high resistance grounding). IEEE Std 141-1993 (Red Book) section 7.2.2 states "There is no arc flash hazard, as there is with solidly grounded systems, since the fault current is limited to approximately 5A." As you can see, it is best to not only ground the neutral, but ground trough High-Resistance (typically 5A) for all systems < 600V, most systems > 600V upto 5kV, and Low-Resistance (typically 200A or 400A) for some systems > 600V upto 5kV, and all systems > 5kV upto 15kV.IEEE Std 142-1991 (Green Book) section 1.4.2 states "Numerous advantages are attributed to grounded systems, including greater safety, freedom from excessive system over-voltages that can occur on ungrounded systems during arcing, resonant or near-resonant ground faults, and easier detection and location of ground faults when they do occur." OK, now that we have established why you need to ground the neutral, let's discuss how to ground the neutral. If you effectively ground the neutral, you have just replaced the hazards with ungrounded systems with new hazards in the form of Arc Flash / Blast Hazards. IEEE Std 141-1993 (Red Book)section 7.2.4 states "A safety hazard exists for solidly grounded systems from the severe flash, arc burning, and blast hazard from any phase-to-ground fault." For this reason, IEEE recommends resistance grounding. IEEE Std 142-1991 (Green Book) section 1.4.3 states "The reasons for limiting the current by resistance grounding may be one or more of the following: 1) To reduce burning and melting effects in faulted electric equipment, such as switchgear, transformers, cables, and rotating machines. 2) To reduce mechanical stresses in circuits and appartus carrying fault currents. 3) To reduce electric-shock hazards to personnel caused by stray ground-fault currents in the ground return path. 4) To reduce the arc blast or flash hazard to personnel who may have accidentally caused or who happen to be in close proximity to the ground fault. 5) To reduce the momentary line-voltage dip occasioned by the clearing of a ground fault. 6) To secure control of transient over-voltages while at the same time avoiding the shutdown of a faulty circuit on the occurrence of the first ground fault (high resistance grounding). IEEE Std 141-1993 (Red Book) section 7.2.2 states "There is no arc flash hazard, as there is with solidly grounded systems, since the fault current is limited to approximately 5A." As you can see, it is best to not only ground the neutral, but ground trough High-Resistance (typically 5A) for all systems < 600V, most systems > 600V upto 5kV, and Low-Resistance (typically 200A or 400A) for some systems > 600V upto 5kV, and all systems > 5kV upto 15kV.