Ground Rod size

Status
Not open for further replies.
Why is it a violation as long as there is other compliant electrodes? Isn't it just a supplemental electrode at that point even though it don't qualify as a stand alone electrode? Sort of like driving a rod at a machine in a plant because the manufacturer wants one, as long as it also has bond to the building electrical grounding system, if that manufacturer only specified a 5 foot rod, so what, you still have other compliant grounding electrodes for the premises wiring as well as a mostly useless piece of metal driven in the earth near the machine.
It's connected to the GES. All connected electrodes must be compliant... even supplementary and auxiliary electrodes.
 
It's connected to the GES. All connected electrodes must be compliant... even supplementary and auxiliary electrodes.
Are we limited to only connecting grounding electrodes to the GES?

Is it wrong to bond a water pipe or building steel that isn't a qualifying electrode to a GEC or make a jumper from another electrode that is qualifying?
 
Thinking it would be safe to drive a new 8 foot rod at there box and run GEC to it,Using two achorn nuts of course.I cant get into the CATV box it has a tamper screw installed,want to use the conductor they left in place on new rod.
 
Are we limited to only connecting grounding electrodes to the GES?

Is it wrong to bond a water pipe or building steel that isn't a qualifying electrode to a GEC or make a jumper from another electrode that is qualifying?
You can't connect non-qualifying electrodes to the GES. Jumpering from a non-qualifying electrode would be a definite no-no. But you can bond non-current-carrying metal. It's a matter of your reasoning and how you go about it. :angel:
 
The 5 foot ground rod that is there now has CATV ground connected from CATV box.Going to replace ground rod with 8 foot rod,re-attach CATV ground,Plus a GEC.
 
The 5 foot ground rod that is there now has CATV ground connected from CATV box.Going to replace ground rod with 8 foot rod,re-attach CATV ground,Plus a GEC.
If their box is mounted to the building siding, I'd shoot for structural steel first. Heck, after that I'd probably yank the existing rod and that's probably all I would do. But if I did install an 8' rod, I'd run #6 copper from building steel to the rod. I believe the bonding jumper for com's is only required to be #10 copper.
 
The box is on building.The building is on a slab,its near an entry door, nearest steel is up and over the door, 20 feet down the siding.It would look like hell.Also I cant easily get into the box,it has a tamper screw that Ive never seen before.I would like to use the ground wire that was provided coming out of the box.Its not very long,so I figured change the rod,and dig up our GES and connect.
 
Check out the Internet for sets of tamper resistant screw bits. I have not seen a totally proprietary one yet, but it is a big world. :)

Sent from my XT1585 using Tapatalk
 
Smart $ it seems simple enough for me to change ground rods,connect the CATV ground wire to the new ground rod.bring over a ground wire from the GES,and connect that to the ground rod as well.Do you see any violation/problem with that set up?
 
Smart $ it seems simple enough for me to change ground rods,connect the CATV ground wire to the new ground rod.bring over a ground wire from the GES,and connect that to the ground rod as well.Do you see any violation/problem with that set up?
I do not.
 
You can't connect non-qualifying electrodes to the GES. Jumpering from a non-qualifying electrode would be a definite no-no. But you can bond non-current-carrying metal. It's a matter of your reasoning and how you go about it. :angel:
Which is what it is if it isn't a qualifying electrode, just a piece of metal that someone wants bonded.

If the utility provider wants that non qualifying rod, I'm not going to stop them, as long as they still have a bond to the premises GES they are still in compliance with NEC IMO.
 
Which is what it is if it isn't a qualifying electrode, just a piece of metal that someone wants bonded.

If the utility provider wants that non qualifying rod, I'm not going to stop them, as long as they still have a bond to the premises GES they are still in compliance with NEC IMO.

I agree. You can bond to anything you want to.
 
You can't connect non-qualifying electrodes to the GES. Jumpering from a non-qualifying electrode would be a definite no-no. But you can bond non-current-carrying metal. It's a matter of your reasoning and how you go about it. :angel:
Which is what it is if it isn't a qualifying electrode, just a piece of metal that someone wants bonded.

If the utility provider wants that non qualifying rod, I'm not going to stop them, as long as they still have a bond to the premises GES they are still in compliance with NEC IMO.
I agree. You can bond to anything you want to.
That's why I stated it the way I did... but as just a hunk of metal, you can't use it to connect grounding [electrode] bonding jumpers, such as the OP'er wants to do after replacing "shorty" with a qualifying rod.
 