It seems to me that the key point is not whether you can bond the GES to non-qualifying electrodes, but whether you can bond between qualifying electrodes via a non-qualifying electrode.
250.54(A) just restricts the use of AL conductors.
250.54(B) is about physical protection.
250.54(E) is about ferrous metal enclosures containing a GEC.
It is not clear to me that a bonding jumper between two qualifying electrodes that passes thru a non-qualifying electrode is prohibited. Maybe it is somewhere else but I am not finding it. I think there is a requirement that GEC be continuous (more or less) but I don't recall there is a similar requirement for bonding jumpers.
250.50 Grounding Electrode System. All grounding electrodes
as described in 250.52(A)(1) through (A)(7) that are
present at each building or structure served shall be bonded
together to form the grounding electrode system.
250.53(C) Bonding Jumper. The bonding jumper(s) used to connect
the grounding electrodes together to form the grounding
electrode system shall be installed in accordance with
250.64(A), (B), and (E), shall be sized in accordance with
250.66, and shall be connected in the manner specified in
250.70.
250.54(A) just restricts the use of AL conductors.
250.54(B) is about physical protection.
250.54(E) is about ferrous metal enclosures containing a GEC.
It is not clear to me that a bonding jumper between two qualifying electrodes that passes thru a non-qualifying electrode is prohibited. Maybe it is somewhere else but I am not finding it. I think there is a requirement that GEC be continuous (more or less) but I don't recall there is a similar requirement for bonding jumpers.