Looked that up,very interesting.
See 90.2(B), if you haven't already.Utility companies don't have to comply with NEC, in particular on their side of the demarc point.
Is this true?
None that I'm aware of.If the broadband ground block is bonded to GES, Is there ever a reason to have a ground block 30 feet inside the building as well.
Would it be compliant to install a IBT on the out side of our building in the following manner. We have manhole with GES 10 feet from building.would like to have #6 copper come from man hole GES ten feet to 8 foot ground rod at outside of building.One acorn nut at the ground rod, pass through the #6 copper up a couple feet to a IBT mounted to our building ?
An IBT has to comply with, among other conditions, the following:trying to leave a place for any other utility that might come along, It looks like a ground rod is acceptable as well for everyone to attach to.
(4) At the service equipment, be securely mounted and
electrically connected to an enclosure for the service
equipment, to the meter enclosure, or to an exposed
nonflexible metallic service raceway, or be mounted at
one of these enclosures and be connected to the enclosure
or to the grounding electrode conductor with a
minimum 6 AWG copper conductor
(5) At the disconnecting means for a building or structure,
be securely mounted and electrically connected to the
metallic enclosure for the building or structure disconnecting
means, or be mounted at the disconnecting
means and be connected to the metallic enclosure or to
the grounding electrode conductor with a minimum
6 AWG copper conductor.
At some point someone has determined that an individual rod can not dissipate any more energy into the earth then a 6 AWG copper conductor can deliver to it.I've always been told that for a ground rod on a service all we would ever need is a #6 copper, Is that correct. I want to add another ground rod to our GES. Looking at 250.66 Im not sure what wire to use.
This is how we install here the pipe is going to the water main the 2 conductors coming out of the top go to the grounded conductor bar in each panel . A total of 2 panels that last wire goes straight through the ibs no splice to a ground rodIs the fact that the broadband box is mounted to our metal building siding an issue with grounding either to building steel or our outside ground rod?
Here's a picture where you can see the whole thingThis is how we install here the pipe is going to the water main the 2 conductors coming out of the top go to the grounded conductor bar in each panel . A total of 2 panels that last wire goes straight through the ibs no splice to a ground rod![]()