Redhorse01
Member
when is the best time for this????? i mean if its raining will it give a bad reading or does it really matter??????? if anyone know's please lend a hand thanks

Unless there is some reason to test them, I would not waste my time. It serves no useful purpose in most cases.Redhorse01 said:when is the best time for this????? i mean if its raining will it give a bad reading or does it really matter??????? if anyone know's please lend a hand thanks![]()
![]()
![]()
haskindm said:The fall-of-potential meter requires the installation of two additional electrodes a pre-determined distance from the ground under test. This may not be possible or practical in many areas, such as a building surrounded by a paved parking lot. It also requires that the grounding electrode be disconnected from the electrical system for the test, which may not be advisable for an occupied building.
For what possible reason would this matter at all?zog said:The IEEE std 142 requires 5 Ohms or less for large commerical or industrial systems
maybe understandable.zog said:and 1 ohm or less for generating or transmission station grounds.
If it matters little what the ground resistance is in the first place, why test every three years?zog said:The NFPA 70B recommends that ground systems are electrically tested every 3 years.
petersonra said:For what possible reason would this matter at all?
maybe understandable.
If it matters little what the ground resistance is in the first place, why test every three years?
I would buy doing a visual inspection of the GEC and bonding wires once a year for obvious damage, but anything past that seems overkill, absent some specific need to do it.
Oh? The only details I've seen from the OP were "ground rods around buildings on a military base". :-?zog said:...the application we are discussing here is 15kV-345kV (or higher)...