Well it doesn't translate. It's all about trade-offs and convenient numbers.So how does that translate to the 6' minimum rod spacing required by the NEC?
* * * * * * * * * * * *
If a high voltage line falls across a 120/240V wire, it's low resistance to Earth that matters.
With lightning, it's low RF impedance to Earth that matters.
* * * * * * * * *
I would think the once spacing is greater than longest rod length, we quickly get into diminishing returns.